"the cans got quite cold while charging.
on the can it said it could take up to 15min for each can to dispense fully."
___________________
Just read a can I keep right at the puter - says all kinds of stuff but not 15 min! Don't take it wrong - there's enough bad info out there to fill the Grand Canyon!
~~~~~~~~~~~
As says on a Johnsen's 12oz - "134a Refrigerant" - For 134a A/C systems only (that's nice)
DO NOT CONNECT CAN TO HIGH PRESSURE SIDE OF SYSTEM OR ANY SYSTEM WITH A PRESSURE HIGHER THAN 170 PSIG. This may cause can to burst - resulting in serious personal injury. Start engine and set air conditioner controls for maximum cooling. Check system with gauge to determine pressure (suction) service port. Charge system only through low pressure side. Hold can upright to charge gas. Use only required amount.
~~~~~~~~~~~~~~
That verbatim from their can not my words.
OK: The reason I'm worried is it took so long and you no doubt (I'm guessing) didn't have compressor jumped to stay engaged to suck in the contents as you would - again when warmer really helps. You usually can just warm the little cans with your hands or if needed have a pan of warm water ready (warm not piping hot) as they will get cold as they deliver their contents. Pretty much the pressure is going from highest to lowest so you need to make the can higher pressure than the vehicle. Temp is close to psi by coincidence with 134a and others too. I have a bunch of nice solid brass can taps and half of those failed to seal properly or dispense properly when new! I worry about the quality of some of the junk out there. Mine are run thru a gauge set as well so I'm watching both pressures and take in and out temps while charging.
The little cans are a pain but I find them for literally a buck now and then at end of season and have bought them all sometimes as it's real product just a hassle vs larger container - usually a 30 pounder.
It may be ok if you are pretty sure no air got sucked in thru leaky connections and it can be charged by pressures when you have a steady higher ambient temp to work with. I'm worried for you right now that it could have too much air introduced and the weight of charge is somewhat unknown. It needs to be close and until system is working hard with lots of observations you really can't tell the performance when cold out. Again - it shouldn't be forced to stay engaged when cold outside or where you are working.
The vacuum: 29.92Hg is a full vacuum at sea level. If your gauges are accurate and you could only pull 25Hg (minus side is measured in inches of Mercury) that's really not all that good. Air has moisture which is the enemy and 25Hg at sea level still isn't a full vacuum which by nature is void of air. {{Air won't compress and moisture can cause acids to build up or frost inside}}
Do you know your altitude? You can call it a full vacuum reducing the #s by 1Hg for each 1,000 ft of elevation +/-.
I can look up your altitude or you can with Google Earth!
Check your vacuum pump against your own gauges without the vehicle. You should be able to plug off your gauges while hooked up and read the capability of the pump. It could also be a gauge inaccuracy??
It's not legal to purposely vent refrigerant so I can't suggest doing that. If you don't have recovery/recycle equipment you are supposed to have any known charge recovered. Give that away and still pay someone or get a machine.
You may vacuum a system devoid of refrigerant to a vacuum. Trace amounts lost are acceptable.
More: There's air in hoses if exposed to atmosphere too. When hooked up to charge source you normally let a spit of refrigerant out of line to know it's purged of air before hooking up. No body's cans or equipment details that minor but real concern especially when using the little cans as you are switch from one to the next instead of one container.
Still More: If the charge is really low now it will cycle on and off with defrost request or mix of anything using defrost. Low charge doesn't move oil well to keep compressor lubed and could hurt it. IMO - if unknown - unplug/disable compressor till it's known ok to operate.
Don't worry so much about the liquid vs gas charging as GM Tech said you are adding to an accumulator which is large and far enough away from compressor. Liquid (can upside down) is just faster. It's not a problem on a warmer day either way but better to use gas only for the finish.
Charge weight is important. You can weigh cans with an accurate scale with any hose or tap so you know how much or a partial one you've used or is left. The can taps frequently won't hold a part can forever when just shut if you leave it for weeks or months for any future use it may be lost.
Egad - Sorry for the "verbose" reply. I only want to see you get this working properly such that it will last its best. Ask away as I'm good at confusing things too
T